Managing NSE 3000 using cnMaestro

NSE 3000 is managed using the cloud-hosted cnMaestro (a management solution from Cambium Networks).

This section covers the following topics:

Claiming an NSE device associated with a site

A device manufacturer serial number (MSN) is required to claim an NSE device. You can find the device MSN at the bottom of the device as shown in Figure 1.

Figure 1  MSN of the NSE device

To claim an NSE device that is associated with a site, complete the following steps:

1. From the home page, navigate to Monitor and Manage.

The System page appears, as shown in Figure 2.

Figure 2  The System page

2. On the left panel, in the Networks section, expand the site panel.
3. Click theactions icon and select Claim Device(s).

The Claim Devices window appears, as shown in Figure 3.

Figure 3  The Claim Devices window

4. From the NSE Group drop-down list, select the required group.

NOTE:  

The selected NSE group is automatically pushed to the device while onboarding.

5. In the Enter field, enter the MSN of the NSE device.
6. Click Claim Devices.

The NSE device that is associated with a site is claimed successfully.

Configuring NSE 3000

To configure NSE 3000 devices, create configuration profiles called NSE Groups.

To create and configure a new NSE 3000 group, navigate to Configuration > NSE Groups and click Add.

Figure 4  Creating NSE groups

For a new NSE group, you must configure parameters using the following tabs:

Basic

Using the Basic tab, you can configure basic group information, such as group name and group scope. You have the option to enable automatic synchronization of the configuration changes for devices associated with the NSE group.

To configure parameters on the Basic Information page, complete the following steps:

1. Navigate to Configuration > NSE Groups and click Add.

The Basic Information page appears, as shown in Figure 5.

Figure 5  The Basic Information page

2. Configure the parameters, as described in Table 1.

Table 1: Parameters on the Basic Information page

Parameter

Description

Name

Name for the NSE group.

This parameter allows a maximum of 64 characters.

This is a mandatory parameter.

Scope

Scope determines the availability of the NSE group across different tenant accounts.

By default, the following options are supported:

  • Shared - Configured NSE group will be available to other tenant accounts.

  • Basic Infrastructure - Configured NSE group will be available only to the Basic Infrastructure user. Other tenant accounts will not have access to the NSE group.

Auto Sync

Specifies whether the configuration changes made to the NSE group are automatically applied to all devices associated with the group.

By default, auto sync is enabled.

3. Click Save.

Management

Using the Management tab, you can configure the profile-related parameters such as time settings and event logging.

To configure parameters on the Management page, complete the following steps:

1. On the NSE Groups > Add New page, select the Management tab.

The Management page appears, as shown in Figure 6.

Figure 6  The Management page

2. Configure the parameters, as described in Table 2.

Table 2: Parameters on the Management page

Parameter

Description

On the Management page, there are Management, Time Settings, and Event Logging sections.

Management

Admin Password

The password used to authenticate the NSE 3000 users who access through SSH or web.

This parameter allows a maximum of 32 characters.

This is a mandatory parameter.

Note: Click the editicon to reset the password.

Time Settings

Time Zone

The time zone based on the installation location of the device.

Select an appropriate time zone from the drop-down list to ensure that the device clock is synchronized with the wall clock time.

NTP Server 1

The IPv4 address or domain name of the primary Network Time Protocol (NTP) server.

NTP Server 2

The IPv4 address or domain name of the secondary or a backup NTP server.

Event Logging

Syslog Server 1

The IPv4 address or the domain name of the syslog server 1.

Port

The port number of the syslog server 1 to which the syslog messages are sent.

Supported values: 1 to 65535.

Syslog Server 2

The IPv4 address or the domain name of the syslog server 2.

Port

The port number of the syslog server 2 to which the syslog messages are sent.

Supported values: 1 to 65535.

Syslog Severity

The logs with the selected severity level that must be forwarded to the server.

The following options are supported:

  • Emergency (Level 0)

  • Alert (Level 1)

  • Critical (Level 2)

  • Error (Level 3)

  • Warning (Level 4)

  • Notice (Level 5)

  • Info (Level 6)

  • Debug (Level 7)

3. Click Save.

Network

Using the Network tab, you can configure LAN ports, VLANs, and static routes.

To configure parameters on the Network page, complete the following steps:

1. On the NSE Groups > Add New page, select the Network tab.

The Network page appears, as shown in Figure 7.

Figure 7  The Network page

2. Configure the parameters, as described in Table 3.

Table 3: Parameters on the Network page

Parameter

Description

On the Network page, there are LAN Ports, VLANs, and Static Routes sections.

LAN Ports

Click the edit icon to modify the configuration of the corresponding LAN port as shown in Figure 8, and click Update to apply the changes.

Name

Name of the LAN port.

This parameter cannot be modified.

Mode

The VLAN mode of the port.

The following options are supported:

  • Access Single VLAN: An access port which places all traffic on its configured VLAN and only passes untagged traffic.

  • Trunk Multiple VLANs: A trunk port which allows the selected port to accept or pass 802.1Q tagged traffic.

Description

A brief description of the LAN port.

VLAN

This parameter is applicable only when the Mode parameter is set to Access Single VLAN.

By default, VLAN value is 1.

VLAN value can be in the range: 1 to 4094

This is a mandatory parameter.

Native VLAN

Indicates that the traffic on the native VLAN is untagged. This parameter is applicable only when the Mode parameter is set to Trunk Multiple VLANs.

The Native VLAN value can be in the range: 1 to 4094

This is a mandatory parameter.

Tag the native VLAN

This parameter is applicable only when the Mode parameter is set to Trunk Multiple VLANs. When Tag the native VLAN parameter is enabled, the native VLAN traffic is tagged with 802.1Q.

Allowed VLANs

This parameter is applicable only when the Mode parameter is set to Trunk Multiple VLANs.

This parameter supports a range or comma-separated list of VLANs. Example: 1-3 or 4, 10, 22

Link Speed Advertisement

Indicates the port speed that must be configured for advertisement.

Default: Auto

The following options are supported:

  • Auto

  • 10 Mbps

  • 100 Mbps

  • 1000 Mbps

Port Duplex

Specifies the mode of port communication. The following options are supported:

  • Full Duplex

  • Half Duplex

Port Speed

Specifies the port speed.

Default: Auto

The following options are supported:

  • Auto

  • 10 Mbps

  • 100 Mbps

  • 1000 Mbps

Shutdown

Enables or disables the port.

By default, this parameter is disabled.

VLANs

Note: You can configure up to 16 VLANs.

To add a new VLAN, click Add New. The Add New VLAN window appears, as shown in Figure 9.

To edit an existing VLAN configuration, click the edit icon and modify the parameters in the Edit VLAN window. Finally, click Update to apply the changes.

VLAN ID

Indicates the VLAN ID.

The VLAN ID value can be in the range: 1 to 4094

This is a mandatory parameter.

Description

Displays the user-configured description for the VLAN.

IP Address

IPv4 address that is assigned to the VLAN.

This is a mandatory parameter.

Subnet Mask

Subnet mask that is assigned to the VLAN.

This is a mandatory parameter.

Management Access

Indicates whether the management access is enabled or disabled.

By default, this parameter is enabled.

Enable Rate Limit

Indicates whether the rate limit is enabled or disabled.

By default, this parameter is disabled.

When you select the Enable Rate Limit check box, the Rate Limit parameter appears.

Rate Limit

Specifies the rate of requests sent or received. This parameter appears only when you enable the Enable Rate Limit parameter.

This parameter supports only integer values.

This is a mandatory parameter.

DHCP mode

The following options are supported:

  • None

  • DHCP Server - When you select this option, the DHCP server-related parameters appear.

  • DHCP Relay - When you select this option, the Relay Server IP address parameter appears.

DHCP Server

In addition to the below parameters, you must also configure the parameters in the DHCP Options and MAC Binding List sections, as shown in Figure 10.

Start IP address

Starting IPv4 address in the range.

This is a mandatory parameter.

End IP address

Ending IPv4 address in the range.

This is a mandatory parameter.

Primary DNS

The primary DNS server for clients on the network.

If the DNS server option is enabled on the NSE, the IPv4 address configured for the VLAN can be provided as the DNS server for the network.

Secondary DNS

The secondary DNS server for clients on the network.

Domain

The DNS search domain for the network.

Lease Time

The DHCP lease expiry time for the DHCP pool (in Days, Hours, and Minutes).

This is a mandatory parameter.

DHCP Options

NSE allows configuration of standard and custom DHCP options.

To add a new DHCP option, click Add New. The Add New DHCP Option window appears, as shown in Figure 11.

To edit an existing DHCP option, click the edit icon and modify the parameters in the Edit DHCP Option window. Finally, click Update to apply the changes.

Option

The following DHCP options are supported:

  • Log server(7)

  • Domain name(15)

  • NTP server(42)

  • Vendor specific information(43)

  • Vendor class identifier(60)

  • TFTP server name(66)

  • Boot file name(67)

  • Proxy auto config(252)

  • Custom

This is a mandatory parameter.

Code

A value for the code.

This parameter allows a maximum value of 254.

This is a mandatory parameter.

Type

The following options are supported:

  • Text

  • IP Address

  • Integer

This is a mandatory parameter.

Value

A value in ASCII.

This is a mandatory parameter.

MAC Binding List

For every DHCP pool configured, the user can bind the client MAC address with an IPv4 address from the network. This enables the client to obtain the same IPv4 address whenever they connect to the NSE device.

Following parameters are required to create the binding list:

  • MAC address of the client

  • IPv4 address from the configured pool

When you set MAC and IP address fields and click Add, the binding of MAC and IP address is added.

Note: Upto 200 MAC to IP address bindings are supported per DHCP pool.

Note: When you bind, the binding IP address should be outside the DHCP pool range.

To add a new MAC binding, click Add New. The Add New MAC Binding window appears, as shown in Figure 12.

To edit an existing MAC binding, click the edit icon and modify the parameters in the Edit MAC Binding window. Finally, click Update to apply the changes.

MAC

The MAC address of the client.

This is a mandatory parameter.

IP Address

The IPv4 address that must be assigned to the client.

This is a mandatory parameter.

Description

Displays the user-configured description.

Import

Imports the MAC bindings.

Note: The CSV file that you import must be in the three-column format, for example, MAC, IP address, and Description.

To import MAC bindings, click Import. The Import MAC Bindings window appears, as shown in Figure 13.

Replace existing list

Indicates whether the imported bindings will overwrite the existing list or append to the list.

  • If enabled, the imported bindings will overwrite the existing list

  • If disabled, the imported bindings will append to the existing list.

By default, this parameter is enabled.

Export

Exports the configured bindings list.

The following options are supported:

  • Export all as CSV

  • Export page as CSV

To export MAC bindings, click Export. The export options appear, as shown in Figure 14.

DHCP Relay

Indicates whether the DHCP relay unicasts the DHCP request to an external DHCP server.

This is a mandatory parameter.

Relay Server IP address

IPv4 address of the external DHCP server.

This is a mandatory parameter.

Static Routes

To add a new route, click Add New. The Add New Route window appears, as shown in Figure 15.

To edit an existing route, click the edit icon and modify the parameters in the Edit Route window. Finally, click Update to apply the changes.

Destination Network

The IPv4 address of the destination network.

This is a mandatory parameter.

Prefix Length

The prefix length for the network address.

This parameter supports integer values and a maximum value of 32.

This is a mandatory parameter.

Next Hop

The next hop IPv4 address for the route.

This is a mandatory parameter.

Exit Interface

The exit interface through which the next hop is reachable.

The following options are supported:

  • WAN-1

  • WAN-2

  • VLAN-1

  • VLAN-10

  • VLAN-20

  • VLAN-30

This is a mandatory parameter.

Metric

The metric for the route.

Figure 8  The Edit Port window

Figure 9  The Add New VLAN window

Figure 10  DHCP Options and MAC Binding List

Figure 11  The Add New DHCP Option window

Figure 12  The Add New MAC Binding window

Figure 13  The Import option in MAC Binding List

Figure 14  The Export option in MAC Binding List

Figure 15  The Add New Route window

3. Click Save.

Groups

Using the Groups tab, you can configure user groups, IP groups, and application groups.

To view the Groups page, complete the following steps:

1. On the NSE Groups > Add New page, select the Groups tab.

The Groups page appears, as shown in Figure 16.

Figure 16  The Groups page

2. Configure the parameters, as described in Table 4.

Table 4: Parameters on the Groups page

Parameter Description
On the Groups page, there are User Groups, IP Groups, and Application Groups sections.

User Groups

User groups are used to group locally configured networks and these groups can be used to associate with policies, especially application rules or DNS rules.

To add a new user group, click Add New. The Add User Group window appears, as shown in Figure 17.

To edit a user group, click the edit icon and modify the parameters in the Edit User Group window. Finally, click Update to apply the changes.

Name

Name for the user group.

This is a mandatory parameter.

Description

Description for the user group.

IP Addresses/Source Subnets

IPv4 addresses or source subnets for the user group.

This is a mandatory parameter.

IP Groups

IP groups are used to group networks originating from the WAN, and can be used to attach port forwarding rules.

To add a new IP group, click Add New. The Add IP Group window appears, as shown in Figure 18.

To edit an IP group, click the edit icon and modify the parameters in the Edit IP Group window. Finally, click Update to apply the changes.

Name

Name for the IP group.

Description

Description for the IP group.

IP Addresses/IP Ranges/Source Subnets

IPv4 addresses, IP ranges, or source subnets for the IP group.

This is a mandatory parameter.

Application Groups

Application groups are used to group applications by using application names or categories, which can then be attached to a policy for permitting or denying access.

To add a new application group, click Add New. The Add New Application Group window appears, as shown in Figure 19.

To edit an application group, click the edit icon and modify the parameters in the Edit Application Group window. Finally, click Update to apply the changes.

Name

Name for the application group.

Description

Description for the application group.

Applications

To add applications to the application group, select the required application(s) from the drop-down list and click Add New. The selected applications are added in the Name list.

Application Name Applications for the new application group.

Categories

To include categories for the new application group, select the required categories.

Categories Categories for the new application group.

Figure 17  The Add User Group window

Figure 18  The Add IP Group window

Figure 19  The Add New Application Group window

3. Click Save.

WAN

Using the WAN tab, you can configure the settings related to the WAN interface.

To configure parameters on the WAN page, complete the following steps:

1. On the NSE Groups > Add New page, select the WAN tab.

The WAN page appears, as shown in Figure 20.

Figure 20  The WAN page

2. Configure the parameters, as described in Table 5.

Table 5: Parameters on the WAN page

Parameter

Description

On the WAN page, there are WAN Configurations, Load Balancing, and Flow Preferences sections.

WAN Configurations

In this section, you can configure the parameters in Connection Health, Dynamic DNS, Link Capacity, Traffic Shaping, Failover Policy, and WAN Speed Test subsections.

The same parameters appear in both WAN-1 and WAN-2 tabs.

IP Address Assignment

Determines the mode of IP address assignment for the WAN interface.

The following options are supported:

  • Dynamic: Dynamically learn the IP address and DNS from the DHCP server.

  • Static: Manually configure the IP address, gateway, and DNS server IP provided by the service provider.

  • PPPoE: When you configure PPPoE, you must provide the username and password of the service provider. While the account name and service name are not mandatory configurations, they may be required if the service provider enforces it. By default, the MTU is set to 1492 and the TCP MSS clamping is enabled. If required, you can also tag the packet on the WAN link to send.

Enable 802.1q VLAN tagging of frames

When this parameter is enabled, 802.1Q tag is inserted with configured VLAN ID for all the packets going out of the WAN interface.

By default, this parameter is disabled.

VLAN ID

This parameter is applicable only when Enable 802.1q VLAN tagging of frames check box is selected.

VLAN ID range: 1 and 4094.

This is a mandatory parameter.

When the 802.1Q header is configured, all transmitted frames are expected to include the 802.1Q header with the same VLAN ID.

Following parameters appear when you select Static from the IP Address Assignment drop-down list.

IP Address

The IPv4 address of the WAN interface.

This is a mandatory parameter.

Subnet Mask

The subnet mask for the IPv4 address of the WAN interface.

This is a mandatory parameter.

Default Gateway

The IPv4 address of the default gateway for the WAN interface.

Primary DNS

The IPv4 address of primary upstream DNS server on this interface.

This is a mandatory parameter.

Secondary DNS

The IPv4 address of secondary upstream DNS server on this interface.

Following parameters appear when you select PPPoE from the IP Address Assignment drop-down list.

Account Controller Name

Name of the account controller.

This parameter allows a maximum of 32 characters.

This parameter is optional.

Service Name

Indicates the service name of the Account Controller.

This parameter allows a maximum of 32 characters.

The service name configuration is optional.

User

User name for PPPoE authentication.

This is a mandatory parameter.

Password

Password for PPPoE authentication.

This parameter is optional.

MTU

MTU for PPPoE interface.

MTU ranges from 500 to 1492 bytes.

Default: 1492 bytes.

TCP MSS Clamping

Indicates whether TCP MSS Clamping is enabled or disabled.

By default, this parameter is enabled.

Additional IP Addresses

WAN IP addresses that are available for source NAT.

Enable Source NAT

Indicates whether the source NAT is enabled or disabled.

When enabled, NSE device will replace the source IP address of the traffic routed from LAN to WAN with the WAN interface IP address.

By default, this parameter is enabled.

Source NAT Rules

Allows user to configure source NAT rules. User can choose the WAN IP addresses from the Additional IP Address for source NAT. User can configure WAN IP address(es) of their choice for source NAT. By default, all the LAN users' traffic will be source NATed to the configured WAN IP address(es). When LAN pool is configured, the traffic from the specified LAN networks will be source NATed to the configured WAN IP address(es).

Note: Source NAT Rules supports up to 16 rules per WAN.

To add a new source NAT, click Add New. The Add New Source NAT Rule window appears, as shown in Figure 21.

Precedence

The precedence value for the source NAT rule.

The precedence value can be between 1 and 150.

This is a mandatory parameter.

LAN Pool

The following options are supported:

  • All

  • IP Group

  • IP Address / Source Subnet

WAN Pool

The following options are supported:

  • Single IP Address

  • Multiple IP Addresses

IP Address

IPv4 address for the WAN pool.

Applicable only when Single IP Address option is selected.

Start IP

Starting IP address in the range.

This parameter is applicable only when Multiple IP Addresses option is selected.

This is a mandatory parameter.

End IP

Ending IP address in the range.

This parameter is applicable only when Multiple IP Addresses option is selected.

This is a mandatory parameter.

IP Group

Select the IP group for the source NAT. IP groups are the ones that you configure in the Groups > IP Groups section.

This parameter is applicable only when IP Group option is selected.

This is a mandatory parameter.

IP Address / Source Subnet

This parameter is applicable only when IP Address / Source Subnet option is selected.

This is a mandatory parameter.

Connection Health

This section is configured to monitor the WAN connection health.

Click the editicon to modify the Monitor Host configuration, as shown in Figure 22. Finally, click Update to apply the changes.

To add a new monitor host, click Add New. The Add New Monitor Host window appears, as shown in Figure 23.

Monitor Host

The hosts used to monitor and collect network traffic data.

Default: 8.8.8.8

This is a mandatory parameter.

Number of Host Failures

The number of monitor hosts that fail to declare the link down.

Default value: 1

The maximum number of monitor hosts that can be configured to fail is 5.

Failure Detect Time

The time period (in seconds) during which the device waits for the response from the monitored host before declaring the link down.

Default: 5. Range: 5 to 60

Interval

The time interval (in seconds) used by the device to check and reach the monitor hosts.

Default: 2. Range: 2 to 10

Timeout

The time period (in seconds) the device waits for a response from the monitor host after which the connection is timed out.

Default: 2. Range: 1 to 10

Dynamic DNS

Enable Dynamic DNS

Indicates whether the dynamic DNS for the interface is enabled or disabled.

By default, this parameter is disabled.

Following parameters appear when Enable Dynamic DNS check box is selected.

DNS Provider

The following options are supported:

  • Cloudflare: Requires secret/access token and zone configuration.

    In the Cloudflare account, navigate to Profile > API Tokens to create a token.

    Following is the recommended setting:

    • Permissions: Zone, DNS, Edit

    • ZoneResource: Include, Specific Zone, <zone name>

  • Godaddy: Requires API key, secret/access token, and zone configuration.

    In the Godaddy account, create an API key at https://developer.godaddy.com/keys

  • Hetzner: Requires secret/access token and zone configuration.

    In the Hetzner account, navigate to Profile > API Tokens and create an access token.

  • Namecheap: Requires password and zone configuration.

    1. In the Namecheap account, navigate to Domains > Free DNS to manage external domains.

    2. Before you update/create a record, a new record of type A must exist. To create a record, navigate to the dashboard, and then navigate to Products > Advanced DNS. Add a new record of type A. On the same page, enable Dynamic DNS and note the password.

  • Noip: Requires server name, username, and password configuration.

  • Route53: Requires API key, secret/access token, and zone configuration.

    1. In the Route 53 account, navigate to route53 > Hosted Zones > Create Hosted Zone to create a zone. Use type Public hosted zone. Note the name servers in hosted zone details and the hosted zone ID.

    2. Navigate to IAM > Users > Create user. Select attach policies directly. Create a policy.

    The following is an example of a policy:

    {

    "Version": "2012-10-17",

    "Statement": [

    {

    "Sid": "",

    "Effect": "Allow",

    "Action": [

    "route53:ListResourceRecordSets",

    "route53:GetChange",

    "route53:ChangeResourceRecordSets"

    ],

    "Resource": [

    "arn:aws:route53:::hostedzone/<ZONE_ID>",

    "arn:aws:route53:::change/*"

    ]

    },

    {

    "Sid": "",

    "Effect": "Allow",

    "Action": [

    "route53:ListHostedZonesByName",

    "route53:ListHostedZones"

    ],

    "Resource": "*"

    }

    ]

    }

    1. Replace ZONE_ID in the policy with the previously noted zone id. Select the new policy for the previously created user.

    2. To create access key, navigate to users, select the user, Security Credentials > Create Access Key.

  • Porkbun: Requires API key, secret/access token, and zone configuration.

    In the Porkbun account, navigate to Account > API Access to create a token. Additionally, the domain configuration much be changed to enable API access.

  • Dyn: Oracle Dyn requires server name, username, and password configuration.

  • DynDNS2 compliant: Requires server name, username, and password configuration.

By default, Noip option is selected.

DNS Hostname

Indicates the DNS host name.

Link Capacity

Uplink

The WAN uplink capacity in Mbps.

Default: 1000. Range: 1 to 1000

This is a mandatory parameter.

Downlink

The WAN downlink capacity in Mbps.

Default: 1000. Range: 1 to 1000

This is a mandatory parameter.

Traffic Shaping

Note: Traffic Shaping supports up to 16 rules per WAN.

To add a new traffic shaping rule, click Add New, the Add New Traffic Shaping Rule window appears, as shown in Figure 24.

Enable Traffic Shaping

Indicates whether traffic shaping is enabled or disabled.

By default, this parameter is disabled.

Precedence

The precedence value for the traffic shaping rule.

The precedence value can be between 1 and 150.

This is a mandatory parameter.

Description Displays a user-configured description for the traffic shaping rule.

Uplink Bandwidth

Indicates the uplink bandwidth in Mbps.

Range: 1 to 1000

This is a mandatory parameter.

Downlink Bandwidth

Indicates the downlink bandwidth in Mbps

Range: 1 to 1000

This is a mandatory parameter.

DSCP

Differentiated Services Code Point (DSCP) can range from 0 to 63, with 0 being the lowest priority and 63 being the highest priority.

Type

Indicates the type of filter rule.

The following options are supported:

  • IP Based – Allows you to configure Protocol parameter as TCP, UDP, or any.

  • Application Based – Allows you to configure Deep Packet Inspection (DPI) Type parameter as Application or Category.

Deep Packet Inspection (DPI) Type

This parameter is applicable only when Type parameter is Application Based.

The following options are supported:

  • Application – Specific type of application within a category.

  • Category – All applications belonging to a category (For example, Social Messaging).

This is a mandatory parameter.

DPI Application

This parameter is applicable only when Deep Packet Inspection (DPI) Type parameter is set to Application.

This is a mandatory parameter.

DPI Category

This parameter is applicable only when Deep Packet Inspection (DPI) Type parameter is set to Category.

This is a mandatory parameter.

Protocol

This parameter is applicable only when Type parameter is IP Based.

The following options are supported:

  • TCP – Match TCP traffic.

  • UDP – Match UDP traffic.

  • any – Match any of the above protocol traffic.

Source IP Address

The source IPv4 address for the shaping rule.

This is a mandatory parameter.

Mask

The subnet mask for the shaping rule.

This is a mandatory parameter.

Port

Displays the source port from which IPv4 address messaging is sent.

This is a mandatory parameter.

Destination IP Address

The destination IPv4 address for the shaping rule.

This is a mandatory parameter.

Mask

The subnet mask for the shaping rule.

This is a mandatory parameter.

Port

Displays the destination port to which IPv4 address messaging is sent.

This is a mandatory parameter.

Failover Policy

Note: Failover Policy supports up to 32 rules per WAN.

To add a new failover policy, click Add New. The Add New Failover Policy window appears, as shown in Figure 25.

Enable Failover Policy

Indicates whether failover policy is enabled or disabled.

By default, this parameter is disabled.

Precedence

The precedence value for the failover policy.

The precedence value can be between 1 and 150.

This is a mandatory parameter.

Description A description for the policy.
Action By default, this parameter is disabled.

Type

The type of failover rule.

The following options are supported:

  • IP Based – Allows you to configure the Protocol parameter as TCP, UDP, or any.

  • Application Based – Allows you to configure Deep Packet Inspection (DPI) Type parameter as Application, Category, or Application Group.

Protocol

This parameter is applicable only when Type parameter is IP Based.

The following options are supported:

  • TCP – Match TCP traffic.

  • UDP – Match UDP traffic.

  • any – Match any of the above protocol traffic.

Source IP Address

The source IPv4 address for the failover rule.

This is a mandatory parameter.

Mask

The subnet mask for the failover rule.

This is a mandatory parameter.

Port

The source port for the failover rule.

This is a mandatory parameter.

Destination IP Address

The destination IPv4 address for the failover rule.

This is a mandatory parameter.

Mask

The subnet mask for the failover rule.

This is a mandatory parameter.

Port

Displays the destination port for the failover rule.

This is a mandatory parameter.

Deep Packet Inspection (DPI) Type

This parameter is applicable only when Type parameter is Application Based.

The following options are supported:

  • Application – Specific type of application within a category.

  • Category – All applications belonging to a category (For example, Social Messaging).

  • Application Group - All applications belonging to a group.

This is a mandatory parameter.

Apply to

This parameter is applicable only when Type parameter is Application Based.

The following options are supported:

  • All

  • User Group

  • IP Address / Source Subnet

User Group

This parameter is applicable when User Group option is selected.

This is a mandatory parameter.

IP Address / Source Subnet

This parameter is applicable when IP Address / Source Subnet option is selected.

This is a mandatory parameter.

WAN Speed Test

Enable WAN Speed Test

Enable or disable the WAN speed test.

By default, this parameter is disabled.

Figure 21  The Add New Source NAT Rule window

Figure 22  The Edit Monitor Host window

Figure 23  The Add New Monitor Host window

Figure 24  The Add New Traffic Shaping Rule window

Figure 25  The Add New Failover Policy window

3. Expand the Load Balancing section and configure the parameters, as described in Table 6.

Table 6: Parameters on the Load Balancing section

Parameter

Description

Load Balancing

WAN-1 Mode

Determines the load balancing mode of device.

By default, the WAN-1 Mode parameter is set to Shared.

The following options are supported:

  • Shared – Enables the WAN link to actively forward a percentage of user traffic. The percentage of user traffic on this link is set via the Traffic Share Percentage parameter.

  • Backup – The WAN link forwards user traffic only when all of the Shared WAN interfaces are down.

  • Disabled – Disables the WAN link from participating in WAN link load sharing, and failover procedures.

Traffic Share Percentage

For the Shared mode, the traffic share percentage must be between 5 and 100.

This is a mandatory parameter.

WAN-2 Mode

Determines the load balancing adjust mode of device.

By default, the WAN-2 Mode parameter is set to Backup.

The following options are supported:

  • Shared – Enables the WAN link to actively forward a percentage of user traffic. The percentage of user traffic on this link is set via the Traffic Share Percentage parameter.

  • Backup – The WAN link forwards user traffic only when all of the Shared WAN interfaces are down.

  • Disabled – Disables the WAN link from participating in WAN link load sharing, and failover procedures.

Traffic Share Percentage

For the Shared mode, the traffic share percentage between 5 and 100.

This is a mandatory parameter.

4. Expand the Flow Preferences section and configure the parameters, as described in Table 7.

Table 7: Parameters on the Flow Preferences section

Parameter

Description

Flow Preferences

Flow preferences support up to 30 rules for both WANs combined.

To add a new flow preference, click Add New. The Add New Flow Preference window appears, as shown in Figure 26.

WAN Interface

The following options are supported:

  • WAN-1

  • WAN-2

Description Provide a description for the flow preference.

Policy

The flow preference policy.

The following options are supported:

  • Flexible – Allow traffic to failover if the preferred WAN link goes down.

  • Strict – Traffic is dropped in strict mode, if the preferred WAN link goes down.

Type

The flow preference type.

The following options are supported:

  • IP Based – Allows you to configure Protocol parameter as TCP, UDP, or any.

  • Application Based – Allows you to configure Deep Packet Inspection (DPI) Type parameter as Application or Category.

Protocol

This parameter is applicable only when Type parameter is IP Based.

The following options are supported:

  • TCP – Match TCP preference.

  • UDP – Match UDP preference.

  • Any – Match any of the above preferences.

Source IP Address

The source IPv4 address for the flow preference.

This is a mandatory parameter.

Mask

The subnet mask for the flow preference.

This is a mandatory parameter.

Port

The source port for the flow preference.

This is a mandatory parameter.

Destination IP Address

The destination IPv4 address for the flow preference.

This is a mandatory parameter.

Mask

The subnet mask for the flow preference.

This is a mandatory parameter.

Port

The destination port for the flow preference.

This is a mandatory parameter.

Deep Packet Inspection (DPI) Type

This parameter is applicable only when Type parameter is Application Based.

The following options are supported:

  • Application – Specific type of application within a category.

  • Category – All applications belonging to a category (For example, Social Messaging).

This is a mandatory parameter.

DPI Application

This parameter is applicable only when Deep Packet Inspection (DPI) Type parameter is set to Application.

This is a mandatory parameter.

DPI Category

This parameter is applicable only when Deep Packet Inspection (DPI) Type parameter is set to Category.

This is a mandatory parameter.

Figure 26  The Add New Flow Preference window

5. Click Save.

Firewall

NSE 3000 firewall allows the user to configure the IP-based and application-based outbound rules, GEO IP filters, port forward rules, one-to-one NAT mappings, and one-to-many NAT mappings. All inbound connections are denied by default. You can configure port forwarding or NAT rules to allow inbound traffic. Outbound traffic is allowed by default. Using application-based outbound rules, users can create rules to block websites without specifying IP addresses or port ranges. Application-based rules allow the user to block a specific type of application within a category or all applications belonging to a category (For example, social messaging).

NOTE:  

Up to 150 outbound firewall rules are supported for an NSE Group including combinations of IP-based and application-based rules.

To configure parameters on the Firewall page, complete the following steps:

1. On the NSE Groups > Add New page, select the Firewall tab.

The Firewall page appears, as shown in Figure 27.

Figure 27  The Firewall page

2. Configure the parameters, as described in Table 8.

Table 8: Parameters on the Firewall page

Parameter

Description

On the Firewall page, there are Outbound Filter Rules, Denial of Service (DoS) Protection, GEO IP WAN to LAN Filters, GEO IP LAN to WAN Filters, Port Forward Rules, NAT One-to-One, NAT One-to-Many, and Device Access sections.

Outbound Filter Rules

To add a new outbound filter rule, click Add New. The Add New Filter Rule window appears, as shown in Figure 28.

Precedence

The precedence value for the filter rule.

The precedence value can be between 1 and 150.

This is a mandatory parameter.

Description

Displays a user-configured description for the filter rule.

Action

Determines the action of filter.

The following options are supported:

  • Permit - Allow traffic matching this filter rule.

  • Deny - Drop traffic matching this filter rule.

Type

The type of filter rule.

The following options are supported:

  • IP Based – Configure Protocol parameter as TCP, UDPICMP or any.

  • Application Based – Configure Deep Packet Inspection (DPI) Type parameter as Application, Category, or Application Group

Protocol

This parameter is applicable only when Type parameter is IP Based.

The following options are supported:

  • TCP: Match TCP traffic.

  • UDP: Match UDP traffic.

  • ICMP: Match ICMP traffic.

  • any: Match any of the above protocol traffic.

Source IP Address

The source IPv4 address for the filter rule.

This is a mandatory parameter.

Mask

The source subnet mask for the filter rule.

This is a mandatory parameter.

Port

This parameter is applicable only when Protocol parameter is TCP or UDP.

Supported values: 1 to 65535 or any

This is a mandatory parameter.

Destination IP Address

The destination IPv4 address for the filter rule.

This is a mandatory parameter.

Mask

The destination subnet mask for the filter rule.

This is a mandatory parameter.

Port

This parameter is applicable only when Protocol parameter is TCP or UDP.

Supported values: 1 to 65535 or any

This is a mandatory parameter.

Deep Packet Inspection (DPI) Type

This parameter is applicable only when Type parameter is Application Based.

The following options are supported:

  • Application – Specific type of application within a category.

  • Category – All applications belonging to a category (For example, Social Messaging).

This is a mandatory parameter.

DPI Application

This parameter is applicable only when DPI Type parameter is set to Application.

This is a mandatory parameter.

DPI Category

This parameter is applicable only when DPI Type parameter is set to Category.

This is a mandatory parameter.

Apply to

This parameter is applicable only when Type parameter is Application Based.

The following options are supported:

  • All

  • User Group

  • IP Address / Source Subnet

User Group

This parameter is applicable when User Group option is selected.

This is a mandatory parameter.

IP Address / Source Subnet

This parameter is applicable when IP Address / Source Subnet option is selected.

This is a mandatory parameter.

Denial of Service (DoS) Protection

IP Spoof

Enable or disable the IP spoof attack protection.

By default, this parameter is disabled.

Smurf Attack

Enable or disable the smurf attack protection.

By default, this parameter is disabled.

IP Spoof Log

Enable or disable IP spoof log messages.

By default, this parameter is disabled.

ICMP Fragment

Enable or disable the fragmented ping attack.

By default, this parameter is disabled.

GEO IP WAN to LAN Filters

GEO IP WAN to LAN filters allows users to configure rules to permit/deny traffic based on the source country of inbound traffic.

Mode

Specifies the mode for GEO IP WAN to LAN filters.

The following options are supported:

  • Allow Only (Deny by default) – Allow traffic coming from the countries that are configured. The traffic coming from the countries which are not part of the configured countries will be dropped.

  • Deny Only (Allow by default) – Block traffic coming from the countries that are configured. The traffic coming from countries that are not part of the configured countries will be allowed.

  • None – Disables the feature. Traffic is allowed from all the countries.

Countries

The source countries from which the traffic originates.

Exceptions

Exceptions allow users to configure source IP address ranges that are allowed in the inbound traffic.

To add a new exception, click Add New. The Add New Exception window appears, as shown in Figure 29.

Start IP

Starting IPv4 address in the range.

This is a mandatory parameter.

End IP

Ending IPv4 address in the range.

This is a mandatory parameter.

GEO IP LAN to WAN Filters

GEO IP LAN to WAN Filters allows users to configure rules to permit/deny traffic based on the destination country of outbound traffic.

Mode

Specifies the mode for GEO IP LAN to WAN filters.

The following options are supported:

  • Allow Only (Deny by default): Allow traffic destined to the countries matching the configured countries. The traffic destined for the countries which are not part of the configured countries will be dropped.

  • Deny Only (Allow by default): Block traffic destined to the countries matching the configured countries. The traffic destined for the countries which are not part of the configured countries will be allowed

  • None: Disables the feature. Traffic is allowed in all countries.

Countries

The destination countries to which the traffic is destined.

Exceptions

Exceptions allow users to configure destination IPv4 address ranges that are allowed in the outbound traffic.

To add a new exception, click Add New. The Add New Exception window appears, as shown in Figure 29.

Start IP

Starting IPv4 address in the range.

This is a mandatory parameter.

End IP

Ending IPv4 address in the range.

This is a mandatory parameter.

Port Forward Rules

Port Forward Rules allow users to forward traffic destined to the WAN Interface IP address of NSE 3000 on a specific TCP or UDP port to any of the LAN IP address. Port Forward Rules provides remote access to internal resources.

To add a new port forward rule, click Add New. The Add New Port Forward Rule window appears, as shown in Figure 30.

WAN

The interface to forward inbound traffic to the internal host.

The following options are supported:

  • WAN-1

  • WAN-2

Description

Displays the user-configured description for the port forward rule.

LAN IP Address

The IPv4 address to which traffic will be forwarded.

This is a mandatory parameter.

LAN Port

The LAN port to which the traffic will be forwarded.

Supported values: 1 to 65535.

This is a mandatory parameter.

Protocol

The protocol of forwarded traffic.

The following options are supported:

  • TCP

  • UDP

Port

The destination port of the incoming traffic on the WAN interface.

Supported values: 1 to 65535.

This is a mandatory parameter.

Apply To

The following options are supported:

  • All

  • IP Group

  • IP Address / Source Subnet

IP Group

This parameter is applicable only when IP Group option is selected.

IP Address / Source Subnet

This parameter is applicable only when IP Address / Source Subnet option is selected.

This is a mandatory parameter.

NAT One-to-One

NAT One-to-One allows users to map an IP address on the WAN side to a LAN IP address. The IP address on the WAN side should be different from any of the WAN interface (WAN-1/WAN-2) IP addresses. NAT One-to-One rules provide remote access to any of the LAN resources.

To add a new NAT one-to-one, click Add New. The Add New NAT One-to-One window appears, as shown in Figure 31.

WAN

The following options are supported:

  • WAN-1

  • WAN-2

Public IP Address

The public IPv4 address on the WAN side that is used to access the LAN resource.

The public IPv4 address is different from the IPv4 address of the WAN (WAN-1/WAN-2) interfaces.

This is a mandatory parameter.

LAN IP Address

The LAN IPv4 address of the server which is hosting the resource.

This is a mandatory parameter.

Protocol

The protocol of the incoming traffic.

The following options are supported:

  • TCP

  • UDP

NAT One-to-Many

NAT One-to-Many provides remote access to internal resources. It maps a public IP address to multiple LAN IPs and ports.

To add a new NAT one-to-many, click Add New, the Add New NAT One-to-Many window appears, as shown in Figure 32.

WAN

The following options are supported:

  • WAN-1

  • WAN-2

Public IP Address

The public IPv4 address on the WAN side that is used to access the LAN resource.

The public IPv4 address is different from the IPv4 address of the WAN (WAN-1/WAN-2) interfaces.

This is a mandatory parameter.

LAN IP Address

The LAN IPv4 address of the server which is hosting the resource.

This is a mandatory parameter.

LAN Port

The LAN Port which is hosting the resource.

This is a mandatory parameter.

Protocol

The protocol of the incoming traffic.

The following options are supported:

  • TCP

  • UDP

Port

The destination port of the incoming traffic on the WAN interface.

This is a mandatory parameter.

Device Access

Respond to ICMP pings from WAN

This parameter is disabled by default.

When enabled, this service is enabled for all the sources, unless specific IP addresses or IP groups are configured in the IP Group and IP Address / Source Subnet parameters.

IP Group

Specifies the IP group for this service.

IP Address / Source Subnet

Specifies the IPv4 address or source subnet for this service.

Figure 28  The Add New Filter Rule window

Figure 29  The Add New Exception window

Figure 30  The Add New Port Forward Rule window

Figure 31  The Add New NAT One-to-One window

Figure 32  The Add New NAT One-to-Many window

3. Click Save.

DNS

NSE 3000 supports DNS-based filters. DNS-based filters allow users to block certain category of websites. From the blocked list, users can still allow certain websites by adding them to the exception list. For example, if user blocks social-media category then all the social websites will be blocked including linkedin.com since linkedin.com belongs to social-media category. Adding linkedin.com to the Exception to filters list will allow access to linkedin.com while blocking other social-media websites.

To configure parameters on the DNS page, complete the following steps:

1. On the NSE Groups > Add New page, select the DNS tab.

The DNS page appears, as shown in Figure 33.

Figure 33  The DNS page

2. Configure the parameters, as described in Table 9.

Table 9: Parameters on the DNS page

Parameter

Description

On the DNS page, there are DNS, Policies, and Hosts sections.

DNS

Enable Built-in DNS Server

Indicates whether the on-board DNS server is enabled or disabled.

By default, this parameter is enabled.

Block external DNS servers

Blocks the client to reach to any external DNS servers.

By default, this parameter is enabled.

Block external DNS exceptions Allows the clients added in the exceptions list to reach to any external DNS servers.

Log to Syslog

Specifies whether the DNS queries received from the client is logged to an external syslog server.

Learn DNS servers from DHCP

Dynamically learns the DNS server IP on WAN.

By default, this parameter is enabled.

When you disable this parameter, the Primary DNS and Secondary DNS parameters are displayed.

Primary DNS

The IPv4 address of the primary upstream DNS server.

Secondary DNS

The IPv4 address of the secondary upstream DNS server.

Local DNS Entries

To add a new local host, click Add New. The Add New Local Host window appears, as shown in Figure 34.

Domain

A domain name for the local host.

This is a mandatory parameter.

IP address

The IPv4 address of the local host.

This is a mandatory parameter.

Conditional Forwarding Rules

To add a new forwarding rule, click Add New. The Add New Forwarding Rule window appears, as shown in Figure 35.

Domain

A domain name for the forwarding rule.

This is a mandatory parameter.

IP address

The IPv4 address of the server to which the DNS query is forwarded.

DNS Filter Mode

Specifies the mode for DNS filtering. The following options are supported:

  • Disabled: Disables DNS filter. By default, this option is selected.

  • Learning: Builds local cache for domain categories but does not filter requests.

  • Filtering: Filters requests based on configuration.

Policies

To add a new policy, click Add New. The Add New Policy window appears, as shown in Figure 36.

Name

Name for the policy.

This is a mandatory parameter.

Description

Description about the policy.

Deny categories

Categories to deny in the following sections:

  • Productivity

  • Privacy

  • Sensitive

  • Misc

  • IT Resources

  • Security

Expand the sections and select individual categories. To select all categories in a section, select the check box provided for the section.

Safe Search Mode

The following options are supported:

  • Disabled: Disables safe search mode. By default, this option is enabled.

  • Moderate: Enable moderate safe search mode.

  • Restricted: Enable restricted safe search mode.

Allow Exceptions (List of Domain Names)

Enter the exempted domain names separated by a comma (,).

Apply to

The following options are supported:

  • All: Apply to all user groups. By default, this option is selected.

  • User Group: Apply to selected user groups.

User Group

This parameter is applicable only when User Group option is selected for Apply to parameter.

This is a mandatory parameter.

Hosts

Hosts section contains two tabs - Safe Search Moderate Hosts and Safe Search Restricted Hosts

The following parameters appear in both the tabs and can be configured as required.

A list of hosts are already added by default. You can modify these hosts by clicking the edit icon or you can add new hosts by clicking Add New in the respective tabs as shown in Figure 37 and Figure 38.

Domain Name

The domain name for the safe search host

This is a mandatory parameter.

IP address

The IPv4 address of the safe search host.

This is a mandatory parameter.

Figure 34  The Add New Local Host window

Figure 35  The Add New Forwarding Rule window

Figure 36  The Add New Policy window

Figure 37  The Add New Safe Search Moderate Host

Figure 38  The Add New Safe Search Restricted Host

3. Click Save.

Threat Protection

Using the Threat Protection tab, you can configure the Intrusion Detection and Prevention system (IDS/IPS) parameters.

NSE 3000 supports IDS/IPS engine. IPS engine uses a series of rules that help define a malicious network activity. IPS engine supports rules from snort and emerging threats. The solution supports both community and licensed rules. The IPS engine uses these rules to find packets that match against them and generates alerts for users.

To configure parameters on the Threat Protection page, complete the following steps:

1. On the NSE Groups > Add New page, select the Threat Protection tab.

The Threat Protection page appears, as shown in Figure 39.

Figure 39  The Threat Protection page

2. Configure the parameters, as described in Table 10.

Table 10: Parameters on the Threat Protection page

Parameter

Description

IDS/IPS

Enable IDS/IPS

Indicates whether IDS/IPS is enabled or disabled.

By default, this parameter is disabled.

Mode

Specifies the IDS/IPS mode.

The following options are supported:

  • Detection – Detects malicious activity and generates alerts for users.

  • Prevention – Detects malicious activity, generates alerts for users, and takes action to prevent attacks.

Rule Type

Specifies the IDS/IPS rule type.

The following options are supported:

  • snort-community – The community rule set is a GPLv2 Talos certified rule set that is distributed free of charge and without any license restrictions. The rules are updated every Tuesday and Thursday.

  • snort-vrt – The Snort Subscriber rule set is developed by Talos research team and is governed by license agreement. The rule set is updated on Tuesday and Thursday. The snort-vrt rule set requires an oinkcode to download and activate rules.

  • emerging-threats open – Consists of signatures contributed from the community. The emerging-threats open rule sets are distributed free of charge.

  • emerging-threats pro – Consists of signatures created as a result of Proofpoint research. The rule sets are governed by license agreement. The emerging-threats pro rule set requires an oinkcode to download and activate the rules.

Rules

Specifies the IDS/IPS rule policy. This parameter is applicable when Rule Type is snort-vrt or snort-community.

The following options are supported:

  • Connectivity – Policy designed to favor device performance over the security controls in the policy.

  • Balanced – This policy is the default policy that is recommended for initial deployments. The policy attempts to balance security needs and performance characteristics.

  • Security – This policy is designed for customer base that is extremely concerned about organizational security. This policy is deployed in networks that have higher security requirements.

Oink Code

This parameter is applicable when Rule Type is snort-vrt or emergency- threats pro.

Category

Categories to select from the Category section. This parameter is applicable when Rule Type is snort-vrt or emergency- threats pro.

Rule Updates

Auto Update

Indicates whether the IDS/IPS rules must be automatically updated or not.

By default, this parameter is disabled.

When Auto Update is enabled, NSE 3000 will periodically download and activate the IDS/IPS rules.

Auto Update Interval

Time interval for the periodic updates of IDS/IPS rules.

The following options are supported:

  • 12 Hrs – Auto updates the rules every 12 hours.

  • 24 Hrs – Auto updates the rules every 24 hours.

IDS/IPS bypass list

List of allowed IPv4 addresses or range of allowed IPv4 addresses.

IDS/IPS operating in prevention mode blocks traffic from a host on detecting malicious traffic from the host.

When an IPv4 address is part of allowed IP addresses, IDS/IPS will not block traffic from the host even when malicious traffic is detected.

3. Click Save.

VPN

NSE 3000 provides an on-board VPN server that allows remote users to establish a connection using the native VPN client supported in most of the operating systems. The VPN server uses the L2TP/IPsec protocol with the IPsec encryption and hashing algorithms. The VPN server maintains a pool of IP addresses and leases the IP addresses from this pool for remote users.

NSE 3000 also provides an on-board RADIUS server that allows authentication and accounting of enterprise and remote users. The RADIUS server maintains user profiles in a central database.

Using the VPN tab, you can configure DNS server, VPN server, and RADIUS server parameters.

To configure parameters on the VPN page, complete the following steps:

1. On the NSE Groups > Add New page, select the VPN tab.

The VPN page appears, as shown in Figure 40.

Figure 40  The VPN page

2. Configure the parameters, as described in Table 11.

Table 11: Parameters on the VPN page

Parameter

Description

On the VPN page, there are Site-to-Site VPN, Client VPN, Users, RADIUS Clients, and VPN sections.

Site-to-Site VPN

IPsec tunnel is a VPN technology that provides a secure, encrypted connection between two devices or networks over the internet or another public network. It uses IPsec protocols to encrypt the traffic between two endpoints, making it difficult for anyone to intercept the communication.

IPsec site-to-site tunnel is used to connect two remote sites for secure communications. NSE allows setting up tunnels both in responder mode and initiator mode. Both, IKEv1 and IKEv2 are supported in the configuration. The default version is IKEv2.

Pre-shared key is the authentication method supported by the device. Each site can have its own pre-shared key. The site is identified by an identifier (string or the IP address of the site). Each site has to be configured with a local and remote site for the tunnel to establish.

To view the IPsec tunnel stats, navigate to the NSE Group > Network > VPN Sites tab, as shown in Figure 42.

To add a new site-to-site VPN, click Add New. The Add New Site-to-Site VPN window appears, as shown in Figure 41.

Enable Site-to-Site VPN

Indicates whether site-to-site VPN is enabled or disabled.

By default, this parameter is disabled.

Following parameters appear when you select Enable Site-to-Site VPN check box.
Name

A name for the new site-to-site VPN.

This is a mandatory parameter.

IKE version

The Internet Key Exchange (IKE) version for the site-to-site VPN. The following options are supported:

  • IKE v1

  • IKE v2

Role

Specifies the role for the tunnels. The following options are supported:

  • Initiator

  • Responder

Default role: Responder

Dead peer detection interval

The interval (in seconds) for detecting dead peers.

Range: 30 - 600 seconds. Default: 120 seconds

This is a mandatory parameter.

Remote ID

The remote ID.

The value of 192.168.50.10 is pre-configured and is not modifiable.

This is a mandatory parameter.

Local ID

The local ID.

This is a mandatory parameter.

Local Subnets

The comma-separated list of local subnets.

This is a mandatory parameter.

Remote Subnets

The comma-separated list of remote subnets.

This is a mandatory parameter.

Remote PSK

The remote PSK.

This is a mandatory parameter.

Local PSK

The local PSK.

This is a mandatory parameter.

The following parameters are common for both IKE Phase 1 and IKE Phase 2.
Encryption

The following options are supported:

  • aes128

  • aes192

  • aes256

  • aes128-gcm16

  • aes192-gcm16

  • aes256-gcm16

  • 3des

Integrity

The following options are supported:

  • md5

  • sha1

  • sha256

DH Group

The following options are supported:

  • 1

  • 2

  • 5

  • 14

  • 15

Key Lifetime

The duration (in hours) for the pre-shared key.

Range: 1 to 24

Client VPN: This section contains the following tabs:

WireGuard: A VPN protocol that is highly secure. It is simpler and more efficient than traditional IPSec.

Enable WireGuard

Indicates whether WireGuard is enabled or disabled.

By default, this parameter is disabled.

Following parameters appear when you select Enable WireGuard check box.
Port

Indicates the WireGuard listen port number.

Default: 51820

This is a mandatory parameter.

Client Pool

Indicates the WireGuard interface IP for the device and the client IPs to be assigned for the WireGuard clients.

This is a mandatory parameter.

Keep Alive

Periodic keep alive packets sent for the configured duration.

Default: 5 seconds

This is a mandatory parameter.

Enable Split Tunnel

Indicates whether the split tunnel is enabled or disabled.

By default, this parameter is disabled.

Note: When you enable split tunnel, only the traffic destined to tunnelled subnets is allowed. You can override the Enable Split Tunnel parameter at the user level.

Tunnelled Subnets

Specifies the list of local subnets in NSE that should be allowed access from the WireGuard clients.

Note: The same Tunnelled Subnets field is auto-populated in the Add New User window. You can edit this field at the user level.

IPSec IKEV2

Enable IPSec IKEV2

Indicates whether IPSec IKEV2 is enabled or disabled.

By default, this parameter is disabled.

Following parameters appear when you select Enable IPSec IKEV2 check box.

Client IP Pool Range Start

Starting IPv4 address in the range.

This is a mandatory parameter.

Client IP Pool Range End

Ending IPv4 address in the range.

This is a mandatory parameter.

L2TP over IPSec

Enable L2TP over IPSec

Indicates whether L2TP over IPSec is enabled or disabled.

By default, this parameter is disabled.

Following parameters appear when you select Enable L2TP over IPSec check box.

Client IP Pool Range Start

Starting IPv4 address in the range.

This is a mandatory parameter.

Client IP Pool Range End

Ending IPv4 address in the range.

This is a mandatory parameter.

IPsec Shared Secret

Enter a pre-shared key string for the IPsec protocol. The shared secret is used between the VPN Client and Server for device authentication.

This is a mandatory parameter.

Enable 2FA

Indicates whether two-factor authentication (2FA) is enabled or disabled.

By default, this parameter is disabled.

VPN Two-Factor Authentication

  1. When you enable two-factor authentication (2FA), scan the QR code to add a 16-digit key to a particular user's Google Authenticator app.

  2. An email is also sent to the configured email address with the QR code and the 16-digit key.

  3. The two-factor authentication gets enabled for the user when the user tries to connect to the NSE device using the remote VPN client from the WAN side. Users on the LAN side do not require two-factor authentication.

Users: This section is common for all the three protocols - WireGuard, IPSec IKEV2, and L2TP over IPSec.

To add a new user, click Add New. The Add New User window appears, as shown in Figure 43.

Email ID

Email ID of the user.
User is either an enterprise user or a remote user.

This is a mandatory parameter.

Password

Password for the user.

This is a mandatory parameter.

Enable WireGuard

Indicates whether WireGuard is enabled or disabled.

By default, this parameter is disabled.

Following parameters appear when Enable WireGuard check box is selected in the Add New User window.
Enable Split Tunnel

Indicates whether split tunnel is enabled or disabled.

By default, this parameter is enabled.

Tunnelled Subnets

Specifies the list of local subnets in NSE that should be allowed access from the WireGuard clients.

Device

Indicates the NSE device.

When you select an NSE device, the device's public key is populated in the [Peer] section of the WireGuard client configuration file.

This is a mandatory parameter.

WAN Interface

WAN Interface of the NSE device.

When you select a WAN interface, the NSE's WAN IP is populated as the endpoint IP in the [Peer] section of the WireGuard client configuration file.

The following WAN Interface options are supported:

  • WAN-1

  • WAN-2

Clients: In this section, you have an option to add a new WireGuard client.

To add a new WireGuard client, click Add New. The Add New WireGuard Client window appears, as shown in Figure 44.

Name

Name for the new WireGuard client.

This is a mandatory parameter.

Auto generate key pair

Generates a public and private key pair for the client. By default, this parameter is enabled.

When this option is enabled, the Client Public Key field is auto-populated with the public key generated for that client.

When this option is disabled, you need to provide the WireGuard client public key generated on the WireGuard client device.

Client Public Key

Public key of the client.

This is a mandatory parameter.

IP Address Auto-generated IP address of the WireGuard client.

Note: You have options to download QR code and configuration file in the Add New WireGuard Client window, as shown in Figure 44.

RADIUS Clients

To add a new RADIUS client, click Add New. The Add New RADIUS Client window appears, as shown in Figure 45.

Name

Name of the RADIUS client.

This is a mandatory parameter.

Secret

The shared secret of the RADIUS client. This is the shared secret (password) that the NAS needs to communicate with the RADIUS server.

This is a mandatory parameter.

Address

The IPv4 address or network address of the RADIUS client.

This is a mandatory parameter.

Prefix Length

The client network prefix length.

This is a mandatory parameter.

VPN

 
VPN Server Interface

The following options are supported:

  • WAN-1 - The first WAN interface on your server.

  • WAN-2 - The second WAN interface on your server.

  • All - Applies to all WAN interfaces.

Figure 41  The Add New Site-to-Site VPN window

Figure 42  The VPN Sites page

Figure 43  The Add New User window

Figure 44  The Add New WireGuard client window

Figure 45  The Add New RADIUS Client window

3. Click Save.

User-Defined Overrides

Using the User-Defined Overrides tab, you can configure the user-defined overrides.

To configure parameters on the User-Defined Overrides page, complete the following steps:

1. On the NSE Groups > Add New page, select the User-Defined Overrides tab.

The User-Defined Overrides page appears, as shown in Figure 46.

Figure 46  The User-Defined Overrides page

2. In the text box, enter the configuration that you want to apply to the device.
3. Click Save.

Configuring WAN in the device UI

In the WAN page, you can configure the device’s IPv4 address based on the IP mode.

NOTE:  

If PPPoE is used as the WAN connection mode as shown in Figure 47, make sure to configure the PPPoE username and password. Once you have configured the PPPoE user name and password, you can proceed to configure the NSE group by providing the same username and password and then attaching the default NSE group to the device.

Figure 47  PPPoE as WAN connection mode

To view and configure the WAN settings, complete the following steps in the device UI:

1. From the main NSE 3000 dashboard page, click WAN tab from the left panel.

The WAN page appears, as shown in Figure 48.

NOTE:  

By default, WAN-1 page appears. You can configure WAN on WAN-1 or WAN-2.

Figure 48  The WAN page

2. Configure the parameters, as described in Table 12.

Table 12: Parameters on the WAN page

Parameter

Description

IP Mode

Determines the network that must be configured to use IPv4 addresses.

The following options are supported:

  • Dynamic

  • Static

  • PPPoE

By default, the Dynamic mode is selected.

VLAN ID

The VLAN ID can range from 1 to 4094.

The VLAN configuration is optional.

When the 802.1Q header is configured, all transmitted frames are expected to include the 802.1Q header with the same VLAN ID.

Following parameters appear only when you select the mode as Static from the IP Mode drop-down list, as shown in Figure 49.

IP Address

The 32-bit binary number that identifies a network element by both network and host.

Subnet Mask

The subnet mask for the destination IP/network for the route.

Gateway

The gateway for the destination IP/network for the route.

DNS

Primary DNS

The IPv4 address of primary upstream DNS server.

Secondary DNS

The IPv4 address of secondary upstream DNS server.

Following parameters appear only when you select the mode parameter as PPPoE from the IP Mode drop-down list, as shown in Figure 50.

Account Name

The name of Access Controller.

This parameter allows a maximum of 32 characters.

This parameter is optional.

Service Name

Service name of Access Controller.

This parameter allows a maximum of 32 characters.

This parameter is optional.

User Name

A user name for PPPoE authentication.

This parameter is mandatory.

Password

A password for PPPoE authentication.

This parameter is optional.

MTU

MTU for PPPoE interface in bytes.

Default: 1492. Range: 500 to 1492

TCP MSS Clamping

Indicates whether TCP MSS Clamping is enabled or disabled.

By default, this parameter is disabled.

Figure 49  Static mode

Figure 50   PPPoE mode

3. Click Save.